So I have been running an EG8010 based inverter for awhile now, and recently connected a circuit which has a clock on it.  The clock was running quite fast, so I compared the frequency of the inverter to the mains and found:

Mains:  59.98Hz
Inverter: 60.18Hz

This would suggest a crystal accuracy of 3000 PPM. Looking at the board, I can see the 2 capacitors connected to the crystal are present.
I would prefer to not take the system down till the weekend, so thought I would float this question.
What kind of frequency accuracy are you seeing with your EG8010 inverter?

Looking on Digikey, I see crystals in the correct package with 10ppm frequency accuracy and stability.  The poorest frequency accuracy crystal I see, is 100ppm.



Thoughts?
Greg
 
noneyabussiness
Guru

Joined: 31/07/2017
Location: Australia
Posts: 527
Posted: 09:23pm 24 Jan 2025
Copy link to clipboard 
Print this post

can I ask... does it matter, your taking .2 hz? the frequency of the grid shifts quite markedly for some (way more than that) with little difference..

maybe it would be easier to tune to device you speak of.. rather than improve the accuracy by a marginal bit on the inverter??
I think it works !!
 
phil99

Guru

Joined: 11/02/2018
Location: Australia
Posts: 3416
Posted: 10:04pm 24 Jan 2025
Copy link to clipboard 
Print this post

I think @oreo's issue is with a synchronous motor clock or mains referenced digital clock accumulating the frequency error.

The short term accuracy of the grid is usually within 0.03 Hz but over the course of a day it is corrected to average exactly 50Hz (60Hz for Canada). So clocks never need adjusting.

Without external correction a crystal oscillator will always drift.
It is possible to pull the frequency of a crystal down a little by adding a few pF in parallel. Experiment with values in the range 1pF to 5.6pF. Larger values than that may cause instability. Use an NPO type for temperature stability.

It still won't be as good as the mains though. For that replace the crystal with a GPS disciplined precision oscillator.
 
wiseguy

Guru

Joined: 21/06/2018
Location: Australia
Posts: 1329
Posted: 12:32am 25 Jan 2025
Copy link to clipboard 
Print this post

I calculated that your inverter is causing a 4.32 minutes error per 24 hours for a mains synched clock, which would annoy me also. Especially being a cumulative error.

Although the mains is not dead accurate over short periods I believe their brief is to ensure there are 5184000 cycles per 24 hours in US (4320000 here) and near midnight the generating authority play a little catchup or slow down to make it so.

I also calculate that the error you are seeing is the equivalent of a 36kHz error in the 12MHz oscillator, yes 100 times worse than a 30part per million initial crystal error. I believe that you can only "pull" a crystal by a few KHz with capacitors so maybe there is something else going on?

I suggest bread-boarding a bare minimum EG8010 circuit with a 12MHz crystal and start with your 60Hz tweaking (monitor SPWM 1 or 2 from memory) whilst nothing else is at play and go from there. If that magnitude of error is still there it points to a possible issue with the internals of the EG8010 ASIC code?

I have heard of people's digital clocks (mains synched) that gain time when their solar inverter is operating so some HF noise was maybe being seen as an extra Hz cycle from time to time, possibly waveform distortion with certain loads is tricking the clock ?

In my opinion you should be able to at least identify where the issue is or/and hopefully get it a lot closer than where you are now?
Edited 2025-01-25 12:09 by wiseguy
If at first you dont succeed, I suggest you avoid sky diving....
Cheers Mike
 
noneyabussiness
Guru

Joined: 31/07/2017
Location: Australia
Posts: 527
Posted: 06:19am 25 Jan 2025
Copy link to clipboard 
Print this post

or spend 10 bucks on a battery clock... no more timing issues with mains...

like I asked, it seems like a unnecessary waste of time... but if you are serious,  just bite the bullet and buy a 10ppm or less crystal ( if possible) and test it(start with simply replacing it on the control board)... there was a thread a few years back, a few went into the accuracy of the eg8010 and crystal combo ( maybe search here or anotherpower) and found it didn't drift all that much.. well the thread died..

also, again unsure if the oscillator would drift too, but the eg8010 has a frequency adjustment feature,  you could try and set it manually and see if you get the same drift... just a thought..
I think it works !!
 
oreo

Senior Member

Joined: 11/12/2020
Location: Canada
Posts: 138
Posted: 04:35am 26 Jan 2025
Copy link to clipboard 
Print this post

Thanks for the suggestions and comments.

  noneyabussiness said  or spend 10 bucks on a battery clock... no more timing issues with mains...

True, and I suppose I could ignore the microwave clock, but the coffee maker makes coffee 5 minutes earlier every day!

As Mike suggested, I set up another one of these EGS002 boards on the bench, and found that the crystal (according to my scope) was running at 16.0006mHz.  As Mike99 suggested, by adding 10pf (my smallest available capacitor) in parallel to both legs of the crystal, brought it down to 15.9998mHz.  

I removed these 2 caps and measured the 8010 output frequency, by capturing the waveform and measuring the period (storage scope).  I measured 60.21376Hz.

I then changed the frequency of the module to 50 hz and repeated the process and measured 50.02Hz.

I can't believe it, but it appears there is a problem with the EG8010 coding when using 60Hz.

If my measurements are correct, I need a 11.958Mhz crystal or crystal oscillator.
Greg
 
oreo

Senior Member

Joined: 11/12/2020
Location: Canada
Posts: 138
Posted: 04:35am 26 Jan 2025
Copy link to clipboard 
Print this post

double post
Edited 2025-01-26 14:47 by oreo
Greg
 
noneyabussiness
Guru

Joined: 31/07/2017
Location: Australia
Posts: 527
Posted: 10:08am 26 Jan 2025
Copy link to clipboard 
Print this post

maybe try the adjustable frequency option. doesn't sound like it's the crystal accuracy after all if the 50hz is right, adjust it to 60hz or as close as and maybe it will keep it better as it will be using a different " set of code " in the chip..

I didn't mean to be rude about the point of this... its just been beaten to death in other threads..
I think it works !!
 
tinyt
Guru

Joined: 12/11/2017
Location: United States
Posts: 564
Posted: 04:39pm 26 Jan 2025
Copy link to clipboard 
Print this post

  oreo said  So I have been running an EG8010 based inverter for awhile now, and recently connected a circuit which has a clock on it.  The clock was running quite fast, so I compared the frequency of the inverter to the mains and found:

Mains:  59.98Hz
Inverter: 60.18Hz

This would suggest a crystal accuracy of 3000 PPM. Looking at the board, I can see the 2 capacitors connected to the crystal are present.
I would prefer to not take the system down till the weekend, so thought I would float this question.
What kind of frequency accuracy are you seeing with your EG8010 inverter?

Looking on Digikey, I see crystals in the correct package with 10ppm frequency accuracy and stability.  The poorest frequency accuracy crystal I see, is 100ppm.



Thoughts?

I also have the same problem. My pool timer uses synchronous motor and it also runs fast. I have to reset the timer after a few days. I am guessing that the EG8010 was originally designed for 50Hz and they just added an option for 60Hz but the result is not as accurate.
 
oreo

Senior Member

Joined: 11/12/2020
Location: Canada
Posts: 138
Posted: 07:31pm 26 Jan 2025
Copy link to clipboard 
Print this post

  noneyabussiness said  I didn't mean to be rude about the point of this...

No worries, I am your typical male.  I am not programmed from the factory to determine if someone is being rude or recognize if I myself am being rude.

Tinyt -thanks for chiming in!  I did find another thread here with complaints about 60hz stability.

Since last night, I have compared my digital clock time, to my watch 3 times 1-5hr spans and got different error differences suggesting frequencies of 60.18, 60.14 and 60.23 Hz.  Average frequency over the whole period is 60.17Hz.  So the inverter seems to be running fast, but not consistently which does not make any sense to me.  Noise would make more sense, but there is no noise when operating just the module on the bench.

My inverter output waveform can look really good depending on the load.  Here is it with the microwave and furnace on.  This is about as bad as I have seen it get.
Note that the frequency measured by the scope jumps between 59.686 and 60.686 hz (2 values).



I think I will monitor the clock error for a longer period.
Greg
 
oreo

Senior Member

Joined: 11/12/2020
Location: Canada
Posts: 138
Posted: 02:28pm 19 Mar 2025
Copy link to clipboard 
Print this post

So I finally got around to trying the variable frequency function of the 8010, which is documented quite well here
Unfortunately, using variable frequency does not allow you to dial in 60hz any more accurately.

So I ordered a SI5131A based oscillator board which should allow me to remove the crystal and feed in the exact frequency I like.  this one

Not sure if I will get around to trying this as I have decided to move away from a 8010 based solution towards an  Arduino based solution.
Greg
 
tinyt
Guru

Joined: 12/11/2017
Location: United States
Posts: 564
Posted: 11:30pm 14 Feb 2026
Copy link to clipboard 
Print this post

  oreo said  So I finally got around to trying the variable frequency function of the 8010, which is documented quite well here
Unfortunately, using variable frequency does not allow you to dial in 60hz any more accurately.

So I ordered a SI5131A based oscillator board which should allow me to remove the crystal and feed in the exact frequency I like.  this one

Not sure if I will get around to trying this as I have decided to move away from a 8010 based solution towards an  Arduino based solution.


Resurrecting this thread as my inverter now powers my entire house loads with appliances that use power line frequency for Clock Displays and they all run too fast to be useful.

Using the SI5131A based oscillator board is too complicated for me, so hopefully there is a simpler solution.

I am still puzzled since the EGS002 uses 12.000 MHz crystal which is an integer multiple of 60Hz or 50Hz.

For base line, I want to know actual grid power line frequency. Since I don't have a frequency counter, I used an arduino/code and and a 6vac step down transformer feeding it through a 10K series resistor, maybe this is good enough. In the serial output, first column is the timer/counter1 value at the rising portion of the sine wave. second column is the resulting calculated ~60Hz. Jitter in values is probably due to time jitter between rising portions of the clamped sinewave. Still readings are close to 60Hz.



I thought that the chinese made crystal on the EGS002 is not precise enough. But I replaced it with crystals from different manufacturers ordered from mouser and still the 60Hz is too high. Below is the result when the arduino/code was fed by 1LO of the EGS002 through a 10K series resistor.


Edited 2026-02-15 09:51 by tinyt
 
phil99

Guru

Joined: 11/02/2018
Location: Australia
Posts: 3416
Posted: 12:15am 15 Feb 2026
Copy link to clipboard 
Print this post

  Oreo said  I can't believe it, but it appears there is a problem with the EG8010 coding when using 60Hz.

If my measurements are correct, I need a 11.958Mhz crystal or crystal oscillator.

With such a large error you may need a lower frequency crystal.
If that value isn't available there may still be companies that can make a crystal to your specification. Probably a bit expensive though.
 
tinyt
Guru

Joined: 12/11/2017
Location: United States
Posts: 564
Posted: 12:25am 15 Feb 2026
Copy link to clipboard 
Print this post

  phil99 said  
  Oreo said  I can't believe it, but it appears there is a problem with the EG8010 coding when using 60Hz.

If my measurements are correct, I need a 11.958Mhz crystal or crystal oscillator.

With such a large error you may need a lower frequency crystal.
If that value isn't available there may still be companies that can make a crystal to your specification. Probably a bit expensive though.


Cost of three (I made 3 inverters) specially cut crystal is beyond my budget. I even tried a vcxo but its adjustment range is not wide enough.

I am now modifying a board to use LTC6900. Will find out soon.
Edited 2026-02-15 10:28 by tinyt
 
poida

Guru

Joined: 02/02/2017
Location: Australia
Posts: 1497
Posted: 12:46am 15 Feb 2026
Copy link to clipboard 
Print this post

I remember driving the EG8010 clock input with a function generator.
it worked and was useful to see what freqs it would still run.
wronger than a phone book full of wrong phone numbers
 
phil99

Guru

Joined: 11/02/2018
Location: Australia
Posts: 3416
Posted: 01:10am 15 Feb 2026
Copy link to clipboard 
Print this post

A regular 32768Hz (2^15) RTC crystal driving a x 365 phase locked loop may be close enough at 11.960320MHz.
 
tinyt
Guru

Joined: 12/11/2017
Location: United States
Posts: 564
Posted: 02:05am 15 Feb 2026
Copy link to clipboard 
Print this post

  phil99 said  A regular 32768Hz (2^15) RTC crystal driving a x 365 phase locked loop may be close enough at 11.960320MHz.


Still too complicated. This one needs only three or two components.

I removed the existing crystal, connected the LTC6900 output to the OSC1 input of the EG8010. (I lost 1 LTC6900 because I sneezed when I was trying to solder it).

According to the LTC6900 data sheet, the resistor value for 12 MHz is 12.5k ohms if my calculation is correct. So I used a fixed 10k resistor and a 5K trimpot. But the resulting 1LO frequency is 71Hz to ~90 Hz with trimpot adjustment.

So, I changed the fixed 10k to 15k.



Here is the arduino/code report. Will continue testing how much it drifts. But looks promising.


 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2284
Posted: 04:05am 15 Feb 2026
Copy link to clipboard 
Print this post

Hope drift is minimal. I have 2 of those dam sync clock devices, usually adjust them once every two weeks, the time difference is around 3 minutes by then.

From memory the EG8010 are a worse than the Nano plus luck of the draw, possibility in both cases.
NANO:Inverter V 8.4ks - Linux AvrDude GUI script V4.1
 
tinyt
Guru

Joined: 12/11/2017
Location: United States
Posts: 564
Posted: 04:59am 15 Feb 2026
Copy link to clipboard 
Print this post

Update:
Frequency(60.0x) did not change much at room temperature for about 2 hours.
So, I used a hair dryer and blew hot air to it and frequency increased to 60.27x.
Frequency went back to 60.0x when it cooled back to room temperature.

The 5K trimpot has its wiper set for 1.46k to get 60Hz. I think I can change it to 2K for finer adjustment with the same number of maximum turns.

The LTC6900 has a TCR of +/-40ppm/C. I don't know the TCRs of the fixed resistor and trimpot. The LTC6900 data sheet recommends using precision metal film resistor for stability.

From mouser, I found these 15k fixed metal film resistors.
YR1B15KCC   +/-15ppm/C  $0.58
PTF5615K000BYEB +/-10ppm/C $5.52
PTF5615K000BZEK  +/-5ppm/C  $7.53

And a 2k Bourns trimpot with a TCR of +/-150ppm/C. So if I use this and the PTF5615K000BZEK  +/-5ppm/C fixed resistor, the trimpot's contribution to total resistance TCR is roughly 10%, I think.

I will also add an on board 5vdc regulator instead of relying on the power board 5vdc supply. This way this modified EGS002 can be swapped between the 3 inverters without re-adjusting the trimpot. But it is another TCR to consider.

It is now more complicated, but everything can still fit on board. But I think this is the best I can do using this device.
Edited 2026-02-15 15:05 by tinyt
 
oreo

Senior Member

Joined: 11/12/2020
Location: Canada
Posts: 138
Posted: 04:19pm 15 Feb 2026
Copy link to clipboard 
Print this post

Nice work!

I reviewed my excel notes from long ago.
I had calculated I needed a frequency of 11.965722 Mhz for the EG8010, for exactly 60hz.
In order to get a clock drift of 1.2 minutes per week, you need a frequency accuracy of 0.09%.
(I think these calculations are correct, but you may want to double check)

Looking at the LTC6900 datasheet:



I am not understanding the datasheet, since the temp drift spec is typical .004%/C but the graph is showing double that.  
Also it seems the device prefers to run on 4v, but that is only introducing .01% deviation over 60C change.

Regarding Resistors.
Taking the formula from the datasheet, you should be at (10Mhz X 20K/16K46) = 12.15Mhz
I calculate the ppm/C of your pot and resistor to be:
(150ppm X 1k46 + 5ppm x 15k)/16k46 = 17.8 ppm

using a cheaper 16k 15ppm resistor and a 1K pot set to 460 ohms would yield:
(150ppm x k46 + 15ppm x 16k)/16k46 = 18.7 ppm

So call it a .0375% over a 20C change.