so how do I connect what is best dc wire to use so fat wire
3 x cindys 2 kw
and one beawindhog.com 4 kw
the usa say i can mount it on a 3 inch pipe
I have found an engineer who will increase my oresent plan fromm 9 metres to 40 metres
re the pdf by enhar ( if u google small wind turbines and take the 4 th heading is pdf for victorian govt and go to page 30 )
 
brucedownunder2
Guru

Joined: 14/09/2005
Location: Australia
Posts: 1548
Posted: 12:15pm 10 Jul 2013
Copy link to clipboard 
Print this post



Gee Tommie,, you're a bit off-frequency trying to work out what you are saying . Sorry ol chum , but thats a fact .

And the way u are talking about 120 foot towers makes me shake a bit ... plus the 3x 4 Kw jobbies --wow ...

Anyhow , you're having fun ,so go for it ,mate.

Bruce.
Bushboy
 
Gizmo

Admin Group

Joined: 05/06/2004
Location: Australia
Posts: 5078
Posted: 12:31pm 10 Jul 2013
Copy link to clipboard 
Print this post

Yeah Tom, not sure what the question is?

Do you mean the tower guy wires, or the electrical wires?
The best time to plant a tree was twenty years ago, the second best time is right now.
JAQ
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 01:19am 11 Jul 2013
Copy link to clipboard 
Print this post

I found an engineer to draw up plans for a 40 metre tower
they have 10 draftsmen and do massive towers for the mining people and all sorts of communication towers
I asked him to make it see saw or something to service turbines
next I have to find help with the other stuff
i need to get a separate meter for wind turbines or I will blow my PFIT tariff after I finally got a resolution to agl stuff up
they may smell a rat if I put 10 kw of turbine thru the meter
re u cannot do more panels then 5 kw to be in pfit scheme
initially victorian govt said 10 kw in 2009 but changed
so after reading the pdf by enhar entitled small windturbines it states not to skimp on towers and that u get 150% more energy with a 120 foot tower
it is easy to get cranes for erection in narre warren vic
I have a substation out front as block is factory block with 3 phase etc
I am trying to get an electric vehicle conversion so substation will be handy for fast filler as I do 200 kms a day
it is hard to find expertise in australia on anything, so i was grateful to find engineers who knew what I was talking about
I have to work out what size copper wire
the fabricator would not work without a plan and I have to get a building permit anyway
I will have 3 of cindys 2 kw toy turbines
and one 4 kw from beawindhog.com
I have seen on some usa sites they use welding wire
a guy on this site designed the square green thing for cindy
i have a friends paddock but it flooded knee high in victorian floods so I do not know what the effect on the turbine wiring would be
there are expensive turbines made for sea installation yes on the sea
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 01:26am 11 Jul 2013
Copy link to clipboard 
Print this post

beawindhog.com are on utube
I have a 4 kw turbine main body of theirs
beawindhog state u can mount it on a 3 inch pipe
so my project involves

3 of cindys 2 kw toy turbines
and one 4 kw from beawind hog.com
so I have tower covered and now have to work out wiring
as gizmo said its a lot of copper wire
 
Downwind

Guru

Joined: 09/09/2009
Location: Australia
Posts: 2333
Posted: 05:36am 11 Jul 2013
Copy link to clipboard 
Print this post

@Tom,

Good to see you are taking your Meds or enabled spell check, or what ever to make your posts partly readable.

I was the person who designed the "green thingy" for OEM (Cindy) and had given a recomendation of 16mm square copper area conductor per phase, for a basic 2kw mill at 9m allowing for some distance to the controller ( "green thingy" ).

When you change the height and the distance between mill and controller, then the cable size (mm2 of copper) also changes to reduce cable loss due to resistance over total distance.

95% of the time the cable size will be far greater than required, but you need to design to the needs of the last 5% to extract max output and to have max control of the mill.

Or to put it another way, if your cable is too small you wont get the same power out the end as you put into it, your losses will be higher in a smaller cable.

Look up Ohms law, and copper cable resistance over distance, and do some calcs of your own on cable size and losses.

Remember your dump load is a resistor, and if you add to much resistance in the cable prior to the dump load, then the mill cannot be fully controlled in high winds.

Otherwise your question reads like...... what size wire do i need to power the space shuttle in orbit?

Pete.
Sometimes it just works
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 06:11pm 12 Jul 2013
Copy link to clipboard 
Print this post

thank you
so is this correct R increases with length
so if I have cable from the hub of turbine at 40 metres tower height

I will overpower cindys green thing u designed

there are a couple of posts on natural gas cars
the problem
all the natural gas facilities are owned by overseas companys who will export the gas onto the world market where they get a better price
the manufacturers are very worried about securing gas
so electric car seems to be best option where u can charge up from your solar garage
gas prices are going to rise in melborune
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 07:27pm 12 Jul 2013
Copy link to clipboard 
Print this post

I = V/R
volts = R x I
I KNOW HOW DO CABLE IS
The resistance, R, of a length of wire is described by the expression:

R = ρL/A
where
ρ = resistivity of the material composing the wire,
L = length of the wire, and
A = area of the conducting cross section of the wire.
THEE IS A CALCULATOR ON A SITE


Closest
AWG Metric
mm2 Circular
inch mm ohm/1000' ohm/km
21 0.50 986.8 0.0363 0.922 10.7290 35.200
18 0.85 1,677 0.0473 1.202 6.3094 20.700
17 1.25 2,467 0.0574 1.457 4.2977 14.100
15 2 3,947 0.0726 1.843 2.6792 8.790
13 3 5,921 0.0889 2.257 1.7861 5.860
11 5 9,868 0.1147 2.523 1.0729 3.520
9 8 15,788 0.1451 3.686 0.6706 2.200
5 20 39,471 0.2294 5.828 0.2679 0.879
ENTER Length in feet or meters Amps
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 07:39pm 12 Jul 2013
Copy link to clipboard 
Print this post

SO RESISTANCE FALLS WITH THE DIAM OF THE WIRE
i USE 6 MM DC CABLE ON MY SOLAR PV PANELS( HAVE TO BUY FROM GERMAN COMPANY HUBER SCHNEIR)
SO SAY I USE ????
i WILL HAVE 3 OF CINDYS 2 KW AND ONE 4 KW FROM BEAWINDHOG.COM IN A ROW
SO WILL HAVE TO HAVE ONE BIG WIRE CONNECTING THEM

Metric Stranded Copper Wire Resistance and Voltage Drop
Size Diameter Resistance @ 77ºF Resistance
for length
(Ohms) Voltage
Drop
(Volts)
Closest
AWG Metric
mm2 Circular
mils inch mm ohm/1000' ohm/km
21 0.50 986.8 0.0363 0.922 10.7290 35.200
18 0.85 1,677 0.0473 1.202 6.3094 20.700
17 1.25 2,467 0.0574 1.457 4.2977 14.100
15 2 3,947 0.0726 1.843 2.6792 8.790
13 3 5,921 0.0889 2.257 1.7861 5.860
11 5 9,868 0.1147 2.523 1.0729 3.520
9 8 15,788 0.1451 3.686 0.6706 2.200
5 20 39,471 0.2294 5.828 0.2679 0.879
ENTER Length in feet or meters Amps
The resistance, R, of a length of wire is described by the expression:

R = ρL/A
where
ρ = resistivity of the material composing the wire,
 
Downwind

Guru

Joined: 09/09/2009
Location: Australia
Posts: 2333
Posted: 08:38pm 12 Jul 2013
Copy link to clipboard 
Print this post


[quote]I will overpower cindys green thing u designed [/quote]

Not exactly correct, the Green thing (controller) will be under powered (not over powered) as the cable resistance will prevent the controller dumping the full power the windmill produces.

Think of the cable as a water pipe, and the windmill pumping water into a tank, the more the wind blows the more water the mill pumps, now if the pipe from the tank (cable) is too small or too long then the volume of water from the tank through the pipe, will be less then the volume of water the mill is pumping, so the tank overflows. (windmill runs away)

What you want is a pipe (cable) big enough to handle the max output of the mill (easy enough) but as pipe is very costly, the bigger the pipe the greater the cost, so you need a pipe correct in size to suit the job, but without going too big to create unnecessary costs.

You talk of 3 mills feeding into one larger cable, that wont work unless the larger cable is after each controller (green thing)

So ...........one windmill............ 3 phase cable............... controller...........DC to bigger cable (3 mills)............... this will work.

NOT......... one windmill..............3 phase cable ...............3 phase to bigger cable (3 mills)............... controller ................ this WILL NOT work
Sometimes it just works
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 01:07am 13 Jul 2013
Copy link to clipboard 
Print this post

THANK U

i HAVE 3 OF CINDYS 2 KW EACH WITH ONE GREEN THING EACH
THE 4 KW FROM BEAWINDHOG (SUSPECT TURBINE MADE AT ANTEROS POST RE HUYAYA FACTORY)
HAS A CONTROLLER
YOUR PLAN WOULD WORK IN THE REVERSE ORDER WOULD IT
FOOTPRINT OF TURBINES

(CINDY 2 KW---- CINDY 2 KW------ CINDY 2KW )--ONE BIG DC CABLE ---CONTROLLER**--3 PHASE CABLE --- BEAWIND HOG 4 KW

HAVE TO GET ANOTHER METER ???? THAT IS A SECOND METER
DO U KNOW HOW TO GET A SECOND METER FROM ELECTRICITY DISTRIBUTOR
SO I NEED TO BUY 3 PHASE CABLE
AND DC CABLE
SO U PUT THE 3 X 2 KW ON ONE BIG CABLE ?
*** DO i PUT A CONTROLLER ON EACH TURBINE
I HAVE 2 TYPES OF CONTROLLERS CINDYS GREEN THINGS X 3
AND ONE BEAWINDHOG
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 01:13am 13 Jul 2013
Copy link to clipboard 
Print this post

(CINDY 2 KW--GREEN THING-- CINDY 2 KW---GREEN THING--- CINDY 2KW ) GREEN THING --ONE BIG DC CABLE ---CONTROLLER**--3 PHASE CABLE --CONTROLLER OF - BEAWIND HOG 4 KW
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 01:15am 13 Jul 2013
Copy link to clipboard 
Print this post

ALSO IN CINDYS BOX CAME A SMALL INVERTER TYPE BOX BUT IT IS NOT AN INVERTER
WHAT IS THIS
 
Downwind

Guru

Joined: 09/09/2009
Location: Australia
Posts: 2333
Posted: 05:36pm 13 Jul 2013
Copy link to clipboard 
Print this post

Ok, Perhaps i misunderstood the "Green thingy" you should have a controller and a dump load, and the green thing might be the dump load, and the inverter looking thing the controller.

Take some photos so we know what you are talking about.
Sometimes it just works
 
tomqu7
Senior Member

Joined: 09/11/2012
Location: Australia
Posts: 168
Posted: 11:22pm 13 Jul 2013
Copy link to clipboard 
Print this post

IT IS A DYNAMIC BRAKING UNIT
i HAVE 3 OF THESE ONE FOR EACH OF CINDYS TURBINES
ONE OF THE TURBINES HAS AN OFF / SWITCH ATTACHED TO WIRE THAT COMES FROM ROTOR
DYNAMIC BRAKING UNIT DOES NOT LOOK LIKE IT IS FOR OUTSIDE USE
SO IF i HAVE TURBINES ALONG DRIVE DO U BRING THE WIRE FROM THE LAST
TURBINE UPTO THE UNDERCOVER CONTROL BOX
DO U PUT THE 3 RESISTORS AND BRAKING UNIT IN ONE PLACE UNDER COVER AND RUN WIRE TO THEM
 
Downwind

Guru

Joined: 09/09/2009
Location: Australia
Posts: 2333
Posted: 11:50pm 13 Jul 2013
Copy link to clipboard 
Print this post

You simply dont grasp how stuff works.
And why are you >>>>> SHOUTING >>>>>> at me with capital text.

All the control gear from Cindy is not suitable to be out in the weather and is intended to be used under protective cover.

Each mill has its own controller and its own dump load, and each mill needs to be suitably wired to its own controller and dump load regardless of where each controller and dump load is located.

The outputs of each controller can be connected together to feed to a common battery or inverter or what ever.

Its best to keep the resistor dump load as close to the controller as suitable. (not lots of meters away)
Sometimes it just works
 