Hi all,

I'd like to check the limit switches on a couple of motorised ball valves & looking for suggestions.

Each valve simply has a SPDT limit switch, so 4 wires back to the micro would do it, but I'd like to get it done on a single wire.

Partially to save on IO pins & also to save on cable cores.
If I did everything the simple way I'd be needing about 12 cores so far.
At the moment I'm using 6.

What I'm thinking is along the lines of the Transmission position switch in my car.
It's basically a 7 position rotary switch with a bunch of resistors in series to create a voltage divider. The contact slider is designed so the is no nul value between positions. (Yes, I've pulled mine apart.....).

What would be the best way to wire these 2 SPDT switches to get a similar resistance scaled output that and be read?

Something that needs to be taken into account is the switch being in the in between position, as the valves take roughly 10 seconds to change position.

A 4 pole rotary switch would be easy, there's either a pole connected, or the Nul between positions.

With the 2 limit switches, either or both of them could be in the nul position.

Thanks

Phil

 
TassyJim

Guru

Joined: 07/08/2011
Location: Australia
Posts: 6632
Posted: 12:37pm 10 Jun 2016
Copy link to clipboard 
Print this post

I think this is what you are after



With the correct values, you can cater for all 9 possible combinations.
These values (in k ohms)
R1 100
R2 22
R3 2
R4 10
R5 1

R6 1


gives
2.856018883
2.972972973
2.049689441

3.126614987
3.267326733
2.185430464

1.605484299
1.641791045
1.314741036

these 9 voltages.
There will be better choices of resistors.
Open circuit cable gives 0 volts.

Jim
VK7JH
MMedit
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 03:32pm 10 Jun 2016
Copy link to clipboard 
Print this post

Thanks Jim,

Will play with the values.

Not getting very accurate voltages off the little solar panel I'm using to read the sun intensity at the moment.

410-550

I've got a 10 Ohm load across the panel & it's maximum output when the sun is vertical is around 1V.

Seems like the sun is usable for water heating once the voltage is above about 300mV.

MicroMite Vs Meter Voltages are a bit like this:-

[Code]
True Voltage MM Reading

300mV 200mV
500mV 390mV
640mV 500mV

[/code]

Would like to add an external reference like in this thread by pmather, but not quite clear on how it is implemented.

Connections etc. Currently just reading the voltage off Pin 4.

Would an LM336 2.5 volt reference be the right thing to use?
Considering I'm looking for say 0-1100mV.
Don't need precision for this, just linearity.
(Do want to use the same for precision on the thermistors I need to read though).

I get a little lost on what connects where & which of the "Vref+ and/or Vref- and/or AVdd" would apply in my case.

I get the function returns an integer 0-1023, but don't quite have my head around the rest.

[Code]
The readADC routine takes two parameters, the pin number to read and the mode.
All relevant pins (pin to read and reference pins) must previously be set as analogue inputs using SETPIN n,AIN

The routine returns the actual ADC count (0-1023), you then need to convert this to a voltage based on the actual values of Vref+ and/or Vref- and/or AVdd as applicable.

So if Vref+ is 2.048V and Vref- is 1.024V and readADC returns 255 in mode-3 then the voltage is 1.024+ 255/1023*(2.048-1.024) = 1.279V
[/code]

Thanks

Phil
 
mikeb

Senior Member

Joined: 10/04/2016
Location: Australia
Posts: 180
Posted: 03:36pm 10 Jun 2016
Copy link to clipboard 
Print this post

Hi Phil,

How far are the valves from the MM ?
Using an analogue input will be prone to noise pickup. The 1K0 resistor (R6) Jim suggests will at least keep a low impedance at the input.
Keep in mind that you are running an antennae out into the field. Be careful of cable run. Route away from all sources which are likely to induce a voltage into the cable.
Filter your input signal in hardware, and software, and use clamp protection at the input.
Are you really that short of pins ?
There are 10 kinds of people in the world.
Those that understand binary and those that don't.
 
TassyJim

Guru

Joined: 07/08/2011
Location: Australia
Posts: 6632
Posted: 03:53pm 10 Jun 2016
Copy link to clipboard 
Print this post

The micromite can resolve about 3.2mV (3.3 / 1024)
If you only have 1 volt to play with, you are getting down to 8 bit precision instead of the full 10 bits.

I used a voltage reference such as the LM336 in my data acquisition setup.
It was connected to an analogue pin and any difference from 2.5V was used as a correction factor for the other readings.

With the limit switch voltage divider, if you are using the same supply as the micromite, there is no correction needed, it's just a ratio.

Jim
VK7JH
MMedit
 
MicroBlocks

Guru

Joined: 12/05/2012
Location: Thailand
Posts: 2209
Posted: 06:17pm 10 Jun 2016
Copy link to clipboard 
Print this post

If the valves are located relatively close together but far away from the MM you could generate a frequency that can be measured by the MM.
A small R/C circuit would be enough.

Microblocks. Build with logic.
 
boss

Senior Member

Joined: 19/08/2011
Location: Canada
Posts: 268
Posted: 05:41am 11 Jun 2016
Copy link to clipboard 
Print this post

@Phil

try this



ADS1115 4x 16bit A/D, I2C, ~$3.50 on Ebay.

Bo
 
matherp
Guru

Joined: 11/12/2012
Location: United Kingdom
Posts: 12083
Posted: 06:44am 11 Jun 2016
Copy link to clipboard 
Print this post

  Quote  Would like to add an external reference like in this thread by pmather, but not quite clear on how it is implemented.


What don't you understand?

To read a value between 0 and say 1.25V use mode 1 (mode=1, Vref+ external and Vref- is AVss/GND ), i.e. connect a 1.25V source to the Vref+ pin (just use a voltage divider off the 3.3V if this is accurate enough for your purposes). The vref+ pin is pin 2 on a 28-pin part and pin 19 on a 44.

Both the pin to be read and the vref+ pin should be set as AIN

Then to convert to a voltage just scale the count value by 1.25/1023Edited by matherp 2016-06-12
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 11:58am 11 Jun 2016
Copy link to clipboard 
Print this post

  matherp said  
  Quote  Would like to add an external reference like in this thread by pmather, but not quite clear on how it is implemented.


What don't you understand?

To read a value between 0 and say 1.25V use mode 1 (mode=1, Vref+ external and Vref- is AVss/GND ), i.e. connect a 1.25V source to the Vref+ pin (just use a voltage divider off the 3.3V if this is accurate enough for your purposes). The vref+ pin is pin 2 on a 28-pin part and pin 19 on a 44.


So to get the most accurate readings from the thermistors in the heat pump unit,
I could take the output of an LM336 to pin 2, the thermistor divider circuit to another & then scale by 3.25/1023.

The difficult part about understanding it probably stems from not completely understanding in layman's term the meaning of the terms like Vref+, Vref-, etc.

Re using a Voltage divider to apply 1.25V to Pin 2.

So, this would result in me spreading the 1023 steps of resolution over 0-1.25 volts,
creating resolution steps of 1.25/1023=1.2mV,

compared to what I'm currently doing and only reading 1.25/3.3*1023=387 steps or resolution over the same range, with 3.2mV resolution.

Phil
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 01:35pm 11 Jun 2016
Copy link to clipboard 
Print this post

  mikeb said   Hi Phil,

How far are the valves from the MM ?
[/quote]
Probably just under 10m by the time the heat pump is moved to the roof.

[Quote]Using an analogue input will be prone to noise pickup......
Keep in mind that you are running an antennae out into the field.....
Be careful of cable run.....
[/quote]

I've got a good supply of old foil shield 8 core data cable,
along with plenty of CAT5,
and also some CAT5 with foil shield & drain.

I'm presuming the 8 is the right choice. Correct? Or would UTP be better?

[Quote]Filter your input signal in hardware.....
[/quote]
0.1µF on input pins suffice?
What is the suggestion for clamping?

[Quote]Are you really that short of pins ?
[/quote]

If I do everything the easy way, everything on it's own pin, it gets tight.

Want to monitor the 5 thermistors on the heat pump for protection;
Evaporator icing, compressor overheat, lost water flow.

Had a couple of scares running it unmonitored & could have killed it.

5 other temp sensors & drive either 3 or 4 240V relays & another 2 on 12v.

I use 2 circulation pumps, as the solar works best at about 8 litres/minute, and the heat pumps is much more efficient with a flow rate of about 15 litres per minute.

One ball valve switches between the solar & the heat pump plumbing & the 2nd one creates a restriction on the water return line, to;

a) Create some head in a stand pipe on the panels &
b) to prevent a siphoning effect on the return line which was causing the panels tubing to suck flat.

Discovered initially that the siphoning effect was causing a 6.5 psi vacuum on the pipes.
Lose 2 pins with an RTC & 2 more with a wireless com port connection;
A couple of status LEDs for easily visible feedback;

I think that count would come to 23.

Phil

 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 02:15pm 11 Jun 2016
Copy link to clipboard 
Print this post

  TassyJim said   The micromite can resolve about 3.2mV (3.3 / 1024)
If you only have 1 volt to play with, you are getting down to 8 bit precision instead of the full 10 bits.

I used a voltage reference such as the LM336 in my data acquisition setup.
It was connected to an analogue pin and any difference from 2.5V was used as a correction factor for the other readings.

With the limit switch voltage divider, if you are using the same supply as the micromite, there is no correction needed, it's just a ratio.

Jim


Understand the limit switch voltage scenario/voltage divider.

It's the thermistors that are giving me issues.
I've got one attached along side a DS18B20 & at times they agree realy well,
but on occasions the thermistor temp drifts off.

Pretty sure its attributed to that Backpack's 3.3V supply that is still less than perfect, but haven't sorted that out completely yet.

Likes to sit around 3.45, but can be anywhere from 3.25 up to 3.65.
Can't see a pattern, & have so far only changed the 2 10µF caps but not the reg.
Have both MCP1700's & AMS1117's here & contemplated whether the AMS1117's might be better due to their higher current rating. Not a straight pin swap though.

I know my ancient Fluke 77 (1985) isn't off the mark, it's sat for a few times on an AD584L voltage reference, & the 5 volt reference sits rock solid on 5.05V on the meter. Accuracy should be 0.3%+/- one digit so 5.035 + one digit would be in tolerance.

Cheers

Phil
 
mikeb

Senior Member

Joined: 10/04/2016
Location: Australia
Posts: 180
Posted: 02:59pm 11 Jun 2016
Copy link to clipboard 
Print this post

Don't have time to sort out that bloody quote button. Maybe you could tell me how to use it.

10m no problem. I remember seeing one of your posts regarding DS18B20's. Why don't you use them instead ? They certainly have sufficient measuring range.

Use the 8 core shielded. Remember to connect the shield at ONE end only otherwise you will set up a 'shorted turn' which is ideal to induce spurious signals into. Think of how a transformer works.
The UTP cable is for differential data networks. That is why it is of a twisted pair construction. Ideal for ethernet and RS485. Besides, it is designed to be terminated with an IDC crimp plug. Not stripped and wired to a terminal. You only have to 'knick' the copper conductor (solid core variety) and the conductor will fail at that point when you bend it.

Put a 10uF tantalum cap in parallel with your 100n cap. You could try to work out the 'passband' performance buy I tend not to bother. The temperature should be a relatively slow moving variable and it should not be detrimental with the time constant of the 10uF cap and a 'lowish' current limiting resistor (4k7 max). Make sure this limiting resistor is on the MM side of Jim's 1k0 to ground otherwise you will set up a voltage divider. You will set up one with R6, in series with R1, in his circuit but you'll just have to account for it in calculations. The prime need is to protect the PIC pin from damaging transients.

For clamping I generally use a device generically named as a 'Transorb'. Google that and you'll get plenty of hits. These are, in essence, a very fast zener diode. Get bi-directional ones and they will protect you against most transients (+\-) you are likely to experience. If you get a lightning strike then you will have bigger concerns than a damaged PIC . Go to Harvey Norman and they will try to sell you a surge protector, as always ,

Thermisters are good, cheap sensors but are nothing like linear in their output.
I note your reply to TassyJim re measuring a DS18B20 alongside a thermister.
DS18B20's are linear across the entire range. Thermister's are not.
Matherp did a great piece on using them correctly utilising the well known Steinhart-Hart equation. Follow this link -Fun with Thermistors.
Unless you wish to retain existing equipment I would ditch the thermisters and use DS18B20 assemblies readily available on eBay. Why not have a dedicated MM, up at the equipment, just to perform tasks associated with the equipment, and run a serial comms connection down to another MM used for display, RTC etc and user input ?
I like to 'Divide and Conquer'. I don't like having to deal with 'low level' analogue signals if I don't have to. Circuit layout becomes critical. The use of a stable reference becomes paramount. Although there are neat tricks for autoranging to maintain resolution. See latest SC for example.
I also don't like having to multiplex an I\O buss, use latches etc when it simply isn't necessary. MM's are cheap as chips. There is nothing wrong with 'Distributed Intelligence'. It also cuts down on the cable run between the equipment and the user. Power and Comms.
Edited by mikeb 2016-06-13
There are 10 kinds of people in the world.
Those that understand binary and those that don't.
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 05:47pm 11 Jun 2016
Copy link to clipboard 
Print this post

  mikeb said   Don't have time to sort out that bloody quote button. Maybe you could tell me how to use it.[/quote]
Pm'ed you re that.

[Quote]10m no problem. I remember seeing one of your posts regarding DS18B20's. Why don't you use them instead ?[/quote]
The heat pump already has them install, in the compressor, evaporator & 2 in the heat exchange unit. Only the ambient one is simple to replace.

[Quote]Use the 8 core shielded. Remember to connect the shield at ONE end.....[/quote]
Yeah, that's what I'm doing.


[Quote]For clamping I generally use a device generically named as a 'Transorb'....
Go to Harvey Norman and they will try to sell you a surge protector, as always [/quote]
I remember some lightning protection devices, from my BHP days....
Most were, umm, a bit BIGGER than the Harvey Norman ones....

[Quote]Thermisters are good, cheap sensors but are nothing like linear in their output.
DS18B20's are linear across the entire range.
Thermister's are not.
Matherp did a great piece on using them correctly utilising the well known Steinhart-Hart equation.[/quote]
Yes!
I'm using the information from Peter's Steinhart conversions post.
Just not sure I've got my co-efficients measured & calculated correctly,
and my 3.3v rail is not a good reference.

[Quote]Unless you wish to retain existing equipment I would ditch the thermisters and use DS18B20 assemblies readily available on eBay.[/quote]
The project's already a monster; Plumbing, pumps, valves; cable, panels, sensors & code.
Might ditch them at a later point in time...

[Quote]Why not have a dedicated MM, up at the equipment, just to perform tasks associated with the equipment, and run a serial comms connection down to another MM used for display, RTC etc and user input ?[/quote]
That's the ultimate plan, but just happy to get things going to start.
Then add some more to the learning curve down the line.

Already plan to let the heat pump have its own MM, with a 20x2 LCD, then read that from the other.

In the end I'd like 3 on various project, with a 7" MicroMite Plus as the central controller, but don't want to try & cope with more than I can chew at this stage.

And I need to stop thinking about other things, like the garden sprinklers, & think I could control them too.....

 
redrok

Senior Member

Joined: 15/09/2014
Location: United States
Posts: 209
Posted: 03:31am 12 Jun 2016
Copy link to clipboard 
Print this post

Hi Phil;
  Phil23 said  Not getting very accurate voltages off the little solar panel I'm using to read the sun intensity at the moment.

410-550

I've got a 10 Ohm load across the panel & it's maximum output when the sun is vertical is around 1V.

Seems like the sun is usable for water heating once the voltage is above about 300mV.

MicroMite Vs Meter Voltages are a bit like this:-

[Code]
True Voltage MM Reading

300mV 200mV
500mV 390mV
640mV 500mV

[/code]Phil
Solar PV cells can do a fairly accurate job of measuring the suns apparent intensity. But there are some constraints.

A PV cell is essentially a "current source". This current is highly linear with the incoming light intensity. However, this linearity is only when the cell voltage is near 0 volts.

As the voltage across the cell is allowed to increase some current begins to flow through the intrinsic P-N junction of the cell. At the extreme, all the current is "self consumed" by its junction at 0.5V to 0.7V. Also PV cells generally have a lot more "Leakage Current" than most diodes leading to more non-linearity at higher voltages.

Anyway, the "best solution" is to use an Op-Amp in a "current to voltage converting" circuit which forces the voltage to 0 volts.
But a "Practical" circuit would be one that kept the voltage less then about 0.2V for a silicon cell using a shunt resistor as you are doing. Apparently 10 ohms is a bit to large. I would guess that about 2 ohms would get the voltage down to 0.1V at an influx of 1000W/m^2.
redrok
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 11:43am 12 Jun 2016
Copy link to clipboard 
Print this post

  redrok said   Hi Phil;

But a "Practical" circuit would be one that kept the voltage less then about 0.2V for a silicon cell using a shunt resistor as you are doing. Apparently 10 ohms is a bit to large. I would guess that about 2 ohms would get the voltage down to 0.1V at an influx of 1000W/m^2.
redrok


I presume you are referring to a single cell in the panel as opposed to the whole cell?

I did get on the roof yesterday & remove the resistor....
Open circuit voltage was useless, as I already knew, about 2400mV with the sun rather low in the afternoon. from memory I think maximum OC voltage is 2.8-2.9.

I was figuring on trying alternate values at the controller end, (easier to poke a resistor in the breadboard, than soldering on the roof).

Tried 27 ohms as a starter & it gave a good figure in my head.
I'm not looking for accurate watts/m² at this point, just a "Sun is bright enough" variable.

Don't intend to make rash decisions with this like pump on/off the moment it sees a cloud, but take it into consideration with other inputs.
 
robert.rozee
Guru

Joined: 31/12/2012
Location: New Zealand
Posts: 2552
Posted: 02:34am 13 Jun 2016
Copy link to clipboard 
Print this post

regarding the original question: motorized valves with limit switches (2 per valve), with approx 10 seconds between limits while valve is in transit; i'd suggest the following:





with both SW1 and SW2 open, about 2.1v will be present at the analog input, with SW1 closed there will be about 1.4v, with SW2 closed there will be about 0.7v. under fault conditions of the wiring from the micromite open-circuit there will be 3.3v at the analog input, while a short will result in 0v. these voltages are what the micromite 'believes' are present, and are independant of Vcc. no external reference or precise Vcc should be needed.

the wiring 'cost' is a twisted pair to each valve, and 1 analog input pin per valve on the micromite. i would recommend against trying to encode more than a couple of switches per analog input.

it is also a very good idea to have the motor travel shut down by a seperate set of contacts on the limit switches - i presume this is built into the motorized valve design? another safety feature is to monitor the motor current.

the below spreadsheet contains the resistor value calculations:

2016-06-13_121906_resistor_values.zip


cheers,
rob :-)
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 12:19pm 05 Jul 2016
Copy link to clipboard 
Print this post

At this point now; motorised ball valve installed.
Courtesy of Teenager on School holidays...




It's 12V DC, polarity reversed to change direction.
SPDT limit switch.

  robert.rozee said   regarding the original question: motorized valves with limit switches (2 per valve), with approx 10 seconds between limits while valve is in transit; i'd suggest the following:





with both SW1 and SW2 open, about 2.1v will be present at the analog input, with SW1 closed there will be about 1.4v, with SW2 closed there will be about 0.7v. under fault conditions of the wiring from the micromite open-circuit there will be 3.3v at the analog input, while a short will result in 0v.[/quote]

Just wondering what values to test for as far as tolerances are concerned?

3.3, 2.1, 1.4 & 0.7 +/- how much?

[Quote]The wiring 'cost' is a twisted pair to each valve, and 1 analogue input pin per valve on the micromite. i would recommend against trying to encode more than a couple of switches per analogue input.[/quote]
That's what I'm planning, 1 valve per pin. Avoid the encoding of multiple valves.


[Quote]It is also a very good idea to have the motor travel shut down by a separate set of contacts on the limit switches - i presume this is built into the motorized valve design?[/quote]

That's correct, the valves have shut down limits built in.


[Quote]Another safety feature is to monitor the motor current.[/quote]

Not sure how I'd implement that.
Was planning on powering the valves from a 12V plug pack that's only powered when the valves need to be changed.

The control board contains 6 relays, all SPDT.

4 Switch 240; Circulation Pump & Heat Pump compressor.
2 will be required to supply & reverse power to the ball valve.




Current pin count must be:-

1 for Temp Sensors.
1 for a flashing Status LED.
2 for Solar Reading; Panel volts & LM336 reference.
6 for Relays
1 for Limit Switches.

It has an RTC, so I'm probably over committed already once I try to get everything connected.

Cheers

Phil.
 
palcal

Guru

Joined: 12/10/2011
Location: Australia
Posts: 2053
Posted: 03:02pm 05 Jul 2016
Copy link to clipboard 
Print this post

Instead of using a solar panel for sun intensity could you use a LDR
Paul.
"It is better to be ignorant and ask a stupid question than to be plain Stupid and not ask at all"
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1667
Posted: 03:39pm 05 Jul 2016
Copy link to clipboard 
Print this post

  palcal said   Instead of using a solar panel for sun intensity could you use a LDR
Paul.


Yes have thought of that & have a couple of LDR modules here, as well as some LUX sensors.

One thing the Solar panel does reasonably well is compensate for low sun angle in the afternoon.

Not needing anything super accurate & will refine things with time.

Cheers

Phil.
 
robert.rozee
Guru

Joined: 31/12/2012
Location: New Zealand
Posts: 2552
Posted: 02:22am 06 Jul 2016
Copy link to clipboard 
Print this post

use something like this:

setpin 2, AIN
do
v=pin(2)
if v<0.4 then
print "short to ground"
elseif v<1.1 then
print "SW2 closed"
elseif v<1.8 then
print "SW1 closed"
elseif v<2.7 then
print "both switches open"
else
print "open circuit"
endif
loop

note that the case of both switches being closed at once is not distinguished from just SW2 closed, but this situation could only occur if there was a mechanical failure in one of the switches.


cheers,
rob :-)Edited by robert.rozee 2016-07-07
 