Hi all,

I found that the measurements returned by sensors (temperature, humidity) or input devices like nunchuk controllers are 'jumping' around the 'real' physical values.

If I do many measurements, add them and divide them by the number of measurements, then I have a chance to get the correct mean value for that physical property.

He is a technique to get "better measurements" from the very beginning by calculating a running mean over the last 'n' measurements. n ist starting from 1 up to an choosen maximum of i.e. 100 or 1000. When n reaches the value of 1000 it will not grow any more. n defines a weight for the next measuremnt, so only a fraction of the difference of the old mean and the new measuremnt gets into the new mean. the longer the sequence is the lower is the weight for the next value.

As an example I took a pico and measured the temperature by 'Pin(temp)'. The running mean M for the temperature is calculated and printed on every cycle of an endless loop. The minimum function 'Min' is not only increasing n by 1 at each cycle, it is limiting n by the maximum value 'Length'.

Example in Picomite:

' running mean - get better measurements

Const Length = 1000  ' up to Length values are counting
Dim M As float = 0.0 ' running mean
Dim n As integer = 0 ' counter [0..Length]


While true do

 n = Min(Length, n + 1)
 M = M + (Pin(temp) - M ) / n
 Print M
 Pause 100

Loop


If you replace the Pin(temp) by your own GPx input, you will certainly get better values than using only a single value. You can replace the While .. Loop by a For ..Next if you like but the strength of this method is within endless or continued measurements.

- andreas
(excuse my bad english, please)
 
phil99

Guru

Joined: 11/02/2018
Location: Australia
Posts: 3419
Posted: 09:30pm 16 Dec 2021
Copy link to clipboard 
Print this post

Excellent, that is a simpler method than the one I was using I shall adopt it.
 
Volhout

Guru

Joined: 05/03/2018
Location: Netherlands
Posts: 6208
Posted: 07:42am 17 Dec 2021
Copy link to clipboard 
Print this post

hi andreas,

Thank you for sharing this. I knew how it works, and have implemented it myself before, but my solution (as with phil99) was not as elegant as this one.
This is much more elegant.

Volhout.
PicomiteVGA PETSCII ROBOTS
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 08:52am 17 Dec 2021
Copy link to clipboard 
Print this post

Hello both phil99 & Volhout,

thank you for the feedback - I'm glad if you can use it!  

-andreas
Edited 2021-12-17 18:54 by andreas
 
Calli
Regular Member

Joined: 20/10/2021
Location: Germany
Posts: 74
Posted: 09:00am 17 Dec 2021
Copy link to clipboard 
Print this post

Hi Andreas,

greets from Germany :)

I like these little tips, thanks!

Carsten
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 09:07am 17 Dec 2021
Copy link to clipboard 
Print this post

Hi Carsten,  you are wellcome!  

-andreas
 
JohnS
Guru

Joined: 18/11/2011
Location: United Kingdom
Posts: 4391
Posted: 10:17am 17 Dec 2021
Copy link to clipboard 
Print this post

I think it effectively weights more recent readings less and less as time goes by - right?

That may in effect make the result quite far from the wanted current value i.e. fail to track changes except with a bigger & bigger lag - right?

If I'm right it's not suitable in various scenarios.

In those cases EWMA (exponentially weighted moving average) may be appropriate.

John
Edited 2021-12-17 20:18 by JohnS
 
Mixtel90

Guru

Joined: 05/10/2019
Location: United Kingdom
Posts: 9267
Posted: 10:35am 17 Dec 2021
Copy link to clipboard 
Print this post

Won't that depend on how fast you want the readings, John? A fluctuating voltage monitor is a different case to something that has thermal lag, for example. Where you need a spot reading you are probably better taking a load of readings in quick succession, ignoring the first few for stability, and then averaging them. EWMA might be better at spotting trends though.
Mick

Zilog Inside! nascom.info for Nascom & Gemini
 
CaptainBoing

Guru

Joined: 07/09/2016
Location: United Kingdom
Posts: 2171
Posted: 11:25am 17 Dec 2021
Copy link to clipboard 
Print this post

it is effective. A bit of code to set a couple of pins high then read them as analogue in.

The first column is the running mean, the second is simply whatever value is present at the time. The first column quickly settles down and within 10 reading is varying by only a couple of mV. the second is predictable all over the place as you would expect with an open input and no processing - all on unbuffered open lines, not terribly fair or even a good test. If I had more time I would put pots and small caps on both lines and see what it renders.

I think, John, you are correct. I think it's ideal to run on the main thread just taking and averaging measurements for when they are needed, where things change moderately - temperature measurement (from analogue sources), battery voltages etc.

Left to run for some time, it is very stable - the 100uV digit hardly changing


' running mean - get better measurements

Const Length = 1000  ' up to Length values are counting
Dim M As float = 0.0 ' running mean
Dim n As integer = 0 ' counter [0..Length]

Pin(27)=1
SetPin 27,DOUT

SetPin 27,AIN

Do

n = Min(Length, n + 1)
M = M + (Pin(27) - M ) / n
Print M,Pin(27)
Pause 100

Loop
>
>
> RUN
0.662366 0.565591
0.582527 0.515591
0.553584 0.498925
0.541667 0.495161
0.535914 0.509677
0.529211 0.492473
0.526574 0.500538
0.523992 0.506452
0.520968 0.491936
0.520323 0.505914
0.518426 0.502151
0.516935 0.491936
0.516708 0.506452
0.515323 0.493548
0.514731 0.494624
0.514482 0.507527
0.513283 0.491936
0.513291 0.5
0.512337 0.495161
0.512312 0.503763
0.511802 0.503763
0.511168 0.489785
0.511267 0.505914
0.510663 0.497312
0.510366 0.494086
0.510463 0.508602
0.509857 0.494086
0.509908 0.497849
0.509807 0.508064
0.509283 0.489785
0.509383 0.504301
0.509056 0.502688
0.508781 0.492473
0.508966 0.508064
0.508602 0.494086
0.508527 0.494086
0.508573 0.507527
0.508206 0.491936
0.508285 0.498925
0.508172 0.506989
0.507894 0.491398
0.508026 0.505376
0.507764 0.502151
0.507625 0.489785
0.507766 0.506989
0.507492 0.493548
0.507527 0.497849
0.507572 0.507527
0.507318 0.49086
0.507398 0.504839
0.507242 0.502151
0.507113 0.489785
0.507233 0.505914
0.507039 0.493548
0.507009 0.496774
0.507085 0.506452
0.506867 0.493548
0.506943 0.503226
0.506871 0.505914
0.506694 0.491936
0.506804 0.505376
0.506651 0.497849
0.506605 0.49086
0.506695 0.50914
0.506493 0.491398
0.50659 0.503226
0.506452 0.498387
0.506388 0.49086
0.506498 0.50914
0.506329 0.49086
0.506421 0.505376
0.50631 0.495161
0.506282 0.494624
0.506343 0.506452
0.506172 0.492473
0.506247 0.497849
0.506228 0.505914
0.506107 0.490323
0.506186 0.505914
0.506089 0.501075
0.50602 0.489247
0.506104 0.509677
0.505972 0.493011
0.506029 0.499462
0.506022 0.507527
0.505902 0.490323
0.505982 0.503763
0.50589 0.496237
0.505854 0.493011
0.50592 0.508064
0.505802 0.491936
0.505861 0.503226
0.505833 0.502688
0.505748 0.488172
0.50584 0.506452
0.505735 0.495161
0.505753 0.494086
0.505777 0.506452
0.505664 0.492473
0.505731 0.502688
0.505685 0.502688
0.505603 0.490323
0.505684 0.504301
0.505588 0.496237
0.505581 0.494086
0.505635 0.508064
0.505527 0.491936
0.505576 0.5
0.505485 0.494086
0.505543 0.504301
0.505522 0.502151
0.505444 0.489785
0.505514 0.505914
0.505428 0.497849
0.505409 0.493011
0.505469 0.508602
0.505376 0.491936
0.505422 0.499462
0.505413 0.507527
0.505332 0.491398
0.505394 0.506452
0.505324 0.501075
0.505289 0.49086
0.505355 0.507527
0.505273 0.493548
0.505321 0.5
0.505241 0.495699
0.505301 0.503763
0.505276 0.503226
0.505215 0.49086
0.505282 0.506452
0.505201 0.494086
0.505219 0.497312
0.505236 0.506989
0.505153 0.492473
0.505206 0.503763
0.50518 0.498387
0.505143 0.490323
0.505191 0.508602
0.505119 0.494086
0.50514 0.498925
0.50513 0.501075
0.505064 0.491398
0.505126 0.506452
0.505061 0.495161
0.505056 0.494624
0.505098 0.508602
0.505028 0.491398
0.505073 0.499462
0.505065 0.504301
0.504995 0.489247
0.505058 0.505914
0.505 0.494624
0.50502 0.501075
0.504991 0.502151
0.504956 0.491936
0.505003 0.507527
0.504951 0.494086
0.50496 0.495161
0.504987 0.508064
0.504916 0.49086
0.504962 0.504839
0.504908 0.497849
0.504891 0.490323
0.504943 0.507527
0.504887 0.494086
0.504913 0.496774
0.504925 0.508064
0.504864 0.49086
0.504915 0.504839
0.50487 0.494086
0.50487 0.496774
0.504898 0.506452
0.504842 0.490323
0.504885 0.503763
0.50486 0.497849
0.504836 0.491936
0.504872 0.50914
0.504818 0.493548
0.504854 0.499462
0.504848 0.505376
0.5048 0.48871
0.50485 0.507527
0.504792 0.491398
0.50483 0.503226
0.504795 0.5
0.504827 0.501075
0.504787 0.496237
0.504782 0.491398
0.504822 0.508602
0.504763 0.493011
0.504794 0.498387
0.504797 0.506989
0.504755 0.49086
0.5048 0.505376
0.504745 0.491936
0.50477 0.502688
0.504757 0.502688
0.504714 0.489785
0.504758 0.505914
0.504716 0.497849
0.504714 0.491398
0.504751 0.507527
0.504704 0.493011
0.504728 0.497849
0.504732 0.507527
0.504685 0.49086
0.50473 0.504839
0.504692 0.494624
0.504695 0.495161
0.504719 0.506989
0.504674 0.49086
0.504705 0.504839
0.50468 0.496774
0.504669 0.492473
0.504699 0.506989
0.504658 0.492473
0.504683 0.497849
0.504694 0.506989
0.50465 0.487097
0.504693 0.504839
0.504657 0.498925
0.504646 0.492473
0.504678 0.506452
0.50464 0.493548
0.504674 0.501075
0.504673 0.505914
0.504638 0.49086
0.504679 0.505914
0.504635 0.494624
0.504645 0.493548
0.504672 0.507527
0.504626 0.491936
0.504659 0.501075
0.504649 0.505914
0.504613 0.490323
0.504655 0.505376
0.504626 0.499462
0.504614 0.49086
0.504648 0.508064
0.504609 0.494624
0.504643 0.498925
0.504635 0.505376
0.504596 0.490323
0.504635 0.506452
0.504607 0.500538
0.504604 0.491398
0.504635 0.508064
0.504599 0.493011
0.504621 0.498925
0.504627 0.508064
0.504585 0.491936
0.504628 0.503763
0.50461 0.496774
0.504594 0.491936
0.504624 0.508064
0.50459 0.490323
0.504618 0.501075
0.504621 0.504839
0.504582 0.492473
0.504616 0.503763
0.50459 0.496237
0.504593 0.494624
0.504617 0.507527
0.504575 0.493011
0.5046   0.503226
0.504577 0.500538
>


EDIT: correct code
Edited 2021-12-17 21:54 by CaptainBoing
 
JohnS
Guru

Joined: 18/11/2011
Location: United Kingdom
Posts: 4391
Posted: 12:26pm 17 Dec 2021
Copy link to clipboard 
Print this post

  CaptainBoing said  Left to run for some time, it is very stable

It is mathematically almost bound to be so - the code divides any change by a big (& ever bigger) number.

For many reasons one would commonly not want largely to ignore recent changes in that way.

For "unbuffered open lines" - er, why? Not my idea of a remotely fair test!

John
 
CaptainBoing

Guru

Joined: 07/09/2016
Location: United Kingdom
Posts: 2171
Posted: 12:35pm 17 Dec 2021
Copy link to clipboard 
Print this post

  JohnS said  
For "unbuffered open lines" - er, why? Not my idea of a remotely fair test!


and I alluded to such in my post. The idea was I wanted to see how varying "noisy" signals were smoothed by the algorithm... job done I'd say
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 03:59pm 17 Dec 2021
Copy link to clipboard 
Print this post

  JohnS said  I think it effectively weights more recent readings less and less as time goes by - right?

That may in effect make the result quite far from the wanted current value i.e. fail to track changes except with a bigger & bigger lag - right?

If I'm right it's not suitable in various scenarios.

In those cases EWMA (exponentially weighted moving average) may be appropriate.

John


Hi John,

averaging allways results in values which are not exact measurements, but they represent the system under test often better than a random error in a measuremnt. You decide over the "lag" by the Length parameter. It could be 1 or 2 ;-)

if n = 1 then M = M + ( newvalue - M ) / 1 = M + newvalue - M = newvalue

That means if n = 1 then the mean M is exactly the measured newvalue, which is correct.

if n = 2 then M = M + ( newvalue - M ) / 2 = M + newvalue/2 - M/2 = M/2 + newvalue/2 = (M + newvalue)/2

I think that should be correct, too.

Now one can show that this is correct for any n+1 if it is correct for n - but not me in a forum post (it's called an inductive proof ;-)

The "Length" parameter decides how adaptive M follows the real measurements. You can take a small one i.e. 3 or 10 if you need more "accurate" values when quick reaction is needed. Or you take large values 1000, 10000, 100000,.. if you have many measurements but want to have a stable, less hysteric system. It depends on the situation i.e. temperature in a room is not changing quickly but a moon rocket needs quick reaction to side winds for navigation.

I used that formula for nunchuck an took 50 as "Length" parameter. The result was a very smooth movement of the cursor, but quickly enough to move a robot arm.

I will look for EWMA you mentioned - that sounds interesting!

-andreas
 
JohnS
Guru

Joined: 18/11/2011
Location: United Kingdom
Posts: 4391
Posted: 04:07pm 17 Dec 2021
Copy link to clipboard 
Print this post

EWMA is often used in industrial systems, automotive applications and so on in my experience.

In effect it gives the oldest value the least weight and the newest the most, whilst at the same time not really trusting the newest is noise-free.

It would make more sense for your program to use a constant 'n' rather than increasing it in the loop. (You refer to something like that in your recent post.) I think constant 'n' is EWMA (mathematically, it's usually written differently).

John
Edited 2021-12-18 03:53 by JohnS
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 08:29pm 17 Dec 2021
Copy link to clipboard 
Print this post

Hi John,

  Quote  It would make more sense for your program to use a constant 'n' rather than increasing it in the loop.


I thought a while about that sentence and came to the conclusion, that I have to explain the method a little further.

There are two phases, when collecting data, measurements, etc. The first phase is when you gather data to fill all the buffers or space you have reserved in your apparatus. In the beginning you have only a single value, later a second one and so on.

After the initial phase you have filled all buffers and space for storage of values and you have to start to throw away information. This is phase 2. Old values have to be discarded and new values come into play.

The algorithm on top respects these two phases. n is increasing step by step but only up to am maximum value "Length" and then n is constand = Length. The trick is the Min() function.

The importand point is, that as log as n < Length, M is always the mean of all values entered during phase 1. It is the same as if you would store all these n < Length values and sum them up and divide them by n. No information is lost - you get the real average of all values entered so far (but without the need of storage!)

When n reaches Length the Min() function guaranties that n will get no larger than Length. n keeps constant now!

The real advantage  of the method is that you only need two variables and one constant to calculate the mean value of a lot of measurements. You get "correct" values just from the beginning.

If you would store the values first into an array, sum them up and divide them by the length of the array - you would have to wait until the array is filled before you get the first result. And you would have to store all these values into your valuable ram!

-andreas
Edited 2021-12-18 06:29 by andreas
 
JohnS
Guru

Joined: 18/11/2011
Location: United Kingdom
Posts: 4391
Posted: 08:53pm 17 Dec 2021
Copy link to clipboard 
Print this post

EWMA doesn't use an array. It just uses the new reading and the old EWMA. Doesn't even need a Length or Min().

I think mathematically yours ends up the same but with the added Length and Min.

John
Edited 2021-12-18 06:55 by JohnS
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 09:31pm 17 Dec 2021
Copy link to clipboard 
Print this post

I modified the program a little to show the 'n' together with the 'M'
The 'sliding window' has now a Length of 10:

> list
' running mean - get better measurements

Dim M As float = 0.0 ' running mean
Dim n As integer = 0 ' counter [0..Max]
Const Length = 10    ' up to 'Length' values are counting

While true do

 n = Min(Length, n + 1)
 M = M + (Pin(temp) - M ) / n
 Print n,M
 Pause 1000

Loop
> run
1       20.01453921
2       19.78041347
3       19.85845538
4       19.89747634
5       19.92088891
6       19.85845538
7       19.81386
8       19.78041347
9       19.80642744
10      19.82723861
10      19.84596867
10      19.86282573
10      19.87799708
10      19.89165129
10      19.90394008
10      19.91499999
10      19.92495392

Min() is no array - it is just the minimum function of MMBasic.

-andreas
Edited 2021-12-18 07:46 by andreas
 
JohnS
Guru

Joined: 18/11/2011
Location: United Kingdom
Posts: 4391
Posted: 08:56am 18 Dec 2021
Copy link to clipboard 
Print this post

I can't test this but something like:

dim ewma as float
const weight = 0.1      'fraction of current reading to use

ewma = pin(temp)
while true do

ewma = (1 - weight) * ewma + pin(temp) * weight
print ewma
pause 1000

loop

(add a loop counter if you wish, but it's not needed)

John
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 10:04am 18 Dec 2021
Copy link to clipboard 
Print this post

Hello John,

your algo works! I would say it weights the "old mean" 90% and the new measurement 10% if you take 0.1 as weight. I programmed this into the pico and it shows good results:

> list
Dim ewma As float
Const weight = 0.1

ewma = Pin(temp)

While true do

 ewma = (1-weight)*ewma + Pin(temp) * weight
 Print ewma
 Pause 1000

Loop
> run
19.03121109
19.0358936
19.04010787
19.04390071
19.04731426
19.00356131
19.0110088
19.01771154
19.02374401
19.02917324
19.03405954
19.03845721
19.04241511
18.99915207
19.00704049
18.96731492
18.97838705


I see a possible problem only, if the first measurement ewma = Pin(temp) should measure a complete wrong value by accident. I suppose then it would take some rounds to get rid of that value.

If I put a Length = 10 into my method, it yields simmilar results:
' running mean - get better measurements

Dim M As float = 0.0 ' running mean
Dim n As integer = 0 ' counter [0..Max]
Const Length = 10    ' up to 'Length' values are counting

Print " n"," Pin(temp)"," running mean"
Print "---------------------------------------"

While true do

 t = Pin(temp)
 n = Min(Length, n + 1)
 M = M + (t - M ) / n
 Print n,t,M
 Pause 1000

Loop

n       Pin(temp)       running mean
---------------------------------------
1       18.60978475     18.60978475
2       18.60978475     18.60978475
3       19.07803624     18.76586858
4       19.07803624     18.8439105
5       18.60978475     18.79708535
6       18.60978475     18.76586858
7       18.60978475     18.74357089
8       19.07803624     18.78537906
9       19.07803624     18.81789652
10      19.07803624     18.8439105
10      19.07803624     18.86732307
10      19.07803624     18.88839439
10      18.60978475     18.86053342
10      18.60978475     18.83545856
10      19.07803624     18.85971632
10      18.60978475     18.83472317
10      19.07803624     18.85905447
10      19.07803624     18.88095265


But now I see a new problem: Why are some measurements identical up to the last digits, then jumping by 0.4 degrees back and forth? Looks like some strange quantisation inside the temperature measurement Pin(temp)?

-andreas
Edited 2021-12-18 20:12 by andreas
 
matherp
Guru

Joined: 11/12/2012
Location: United Kingdom
Posts: 12083
Posted: 10:30am 18 Dec 2021
Copy link to clipboard 
Print this post

From the RP2040 errata
Differential nonlinearity (acronym DNL)
Effective number of bits (ENOB)

 
Solar Mike
Guru

Joined: 08/02/2015
Location: New Zealand
Posts: 1255
Posted: 11:20am 18 Dec 2021
Copy link to clipboard 
Print this post

>>Looks like some strange quantisation inside the temperature measurement Pin(temp)?

Not helped by the ADC reference being a very noisy 3.3v switching supply; I have had to use a LM4040 shunt reference connected to the ADC Ref pin to get more stable results. Even better turn off the internal 3.3V switcher and use an external 3.3V linear regulator. Kind of defeats the use of a cheap CPU...

Mike
 